Handyman said:
Is the difference between flow and return water temperatures relevant to the efficiency of the system? If so, why? The system in question is a sealed system heated by a condensing boiler.
Non-condensing boilers were designed to operate at high temperatures and a high return temp so as
NOT to condense. The peripheral equipment was designed around this, with 70C return temperatures required from Cylinders and radiators, which also sepecified a Delta T (temp differential) of 10C. The boilers are designed for 80C flow and 70C return – why they put adjustable boiler stats on is a mystery. I have seen some boilers corrode inside that are condensing because the stat was set too low by the user who though they were saving gas.
Condensers are the opposite. You keep the return temperatures from cylinders and radiators as low as possible, using quick recovery cylinders and larger rads. Although in 95% of cases lower temp in rads doesn’t make that much difference in existing rads designed for a delta T of 10C. Most decent condensing boilers are designed with a Delta T of 22-25C. A boiler can only raise the temp of the water a certain level, let’s say 25C, and the temp differential (Delta T) is roughly set to this. The heat exchanger is also designed to cope with this delta T too.
So increasing the delta T it may cause long term heat exchanger harm. They don't over engineer the heat exchanger, as doing so would raise costs and boiler price.
Always keep within the Delta T. With one boiler I was putting on a heat bank I contacted the makers who said that as the boiler was direct to the heat bank and always at full water flow through the heat exchanger (many are not at full flow because of TRVs closing), I could raise to 29C from 25C. I did some tests and the boiler raised the water 28C, so I set the delta T to 28C. That is I set the TMV flow/return blender to 47C, when I knew the boiler would pump into the top of the cylinder 75C, the Heat Bank setpoint.
BTW, I have gained extra efficiencies from a non-condensing boiler having a TMV on the return set to just above condensing dew point – 60C. Lower temp and no condensing. Set to delta T of 10C, 70-60C.