Fluctuating pressure on a system boiler.

S

Soggy_weetabix

Just wondering if anyone has experienced the same problem:

Glowworm System Boiler 18hxi I think. Could be wrong on the model.
Pressure at cold: 1 Bar
Pressure raises to 3 Bar as sytem heats up and prv blows (obviously.)

Check expansion vessel. Air released when operating the valve, so out comes the foot pump to check the pressure.

A fraction under 1 bar is measured, so it appears the e/v is charged correctly, but not tactually taking up any expansion.

This is the 3rd time ive had this fault on this boiler, and have remedied it by plumbing in a new expansion vessel externally on the system, charged at exactly the same pressure as the one on the boiler.

Once done, we're tickaty boo again.

David
 
Sponsored Links
Pipe to expansion vessel blocking or partially blocking. Thus in effect no expansion vessel.
 