We have had a free electrical check flyer come in through the door from our current provider so may take them up on it, to get an idea of what they think.
Free electrical checks are worth every penny you pay for them.
Don't get me wrong, I see great merit in a full PIR.
However, we do free electrical checks and they are useful on their own.
I did one today.
A 17th board on what looked like a PME supply.
But then I got 13.9 Ohms Zs.
So is it PME?
Looked at the EIC. Badly filled out (just a tick for r1+r2) and claiming a rod resistance of 202 Ohms, later described as "on the limit"...
But then, later in the cert, a Ze of 15.8???
Anyhow, the cut-out was not labelled PME and the EIC mentioned a rod which did not have an inspection chamber.
Could I find it? Could I bu**ery!!
So, we have a TT supply with an earth connection to the cut-out, no rod visible & a Ze of 13.9.
PEB's to gas and another to a pipe which disappears into a concrete floor, which the customer insists has a stopcock buried in it...
So I "AT RISK" the installation as the earthing seems to be derived from the supply pipework.
Wanted to talk to the installer of the new board, but he would not answer his phone.