Hey all.
I'm just about to install a Triton Martinique 9.5kw shower, a few queries....
CU is an older Qwikline - 100A mains switch. No RCD present at the moment.
After reading through various posts, i gathered that I would need a 45A MCB. However, I've been told buy my local wholeseller that Qwikline don't make a 45A MCB, only a 40A + 50A. So, i'm assuming 50A is the way to go?
I've also been generiously donated a seperate Wylex Shower RCD, 63A + 30mA, to run along side the CU.
So, my questions are, is this installation acceptable? i.e. Purcasing a 50A MCB, connecting from the MCB on to the RCD, then onto Pull Switch, Shower etc etc.
And, what size cable should I be using? Cable run is about 6 Metres, 4 of which will be clipped.
Personally, i'd rather lean on the side of caution, and go for 16mm, but i'd like a educated opinion.
I know some will say, replace the board. But, if I've only got to pay for an MCB, i'd rather go that way.
Many thanks in advance.
I'm just about to install a Triton Martinique 9.5kw shower, a few queries....
CU is an older Qwikline - 100A mains switch. No RCD present at the moment.
After reading through various posts, i gathered that I would need a 45A MCB. However, I've been told buy my local wholeseller that Qwikline don't make a 45A MCB, only a 40A + 50A. So, i'm assuming 50A is the way to go?
I've also been generiously donated a seperate Wylex Shower RCD, 63A + 30mA, to run along side the CU.
So, my questions are, is this installation acceptable? i.e. Purcasing a 50A MCB, connecting from the MCB on to the RCD, then onto Pull Switch, Shower etc etc.
And, what size cable should I be using? Cable run is about 6 Metres, 4 of which will be clipped.
Personally, i'd rather lean on the side of caution, and go for 16mm, but i'd like a educated opinion.
I know some will say, replace the board. But, if I've only got to pay for an MCB, i'd rather go that way.
Many thanks in advance.