Hi all I was moving my tv set and there was quite a lot of tangled unused cables which I wanted to remove, as i was in a rush I rather stupidly cut the cable to the extension lead which resulted in a loud bang and bright flash as well as a big hole in my cable snips, this tripped out the 32 amp ring circuit breaker, but when I tested the fuse on the extension lead and it still had continunity, it never blew.
So my question is why did the mcb trip faster than the 13 fuse take to blow in the plug? The rcd never tripped either, just the 32amp mcb tripped, but the fuse in the plug to the lead I daftly cut was still intact.
Just curious, and yes I know I was daft, never got shocked luckily just a bit shaken.