Fuse in neutral blows when machine turned off
7 Dec 2007
Hi all, a strange fault for you I hope, something to get those little grey cells working ;)
A PLC power supply that has a 2A fuse in the live and a 2A fuse in the neutral...an Italian design.
Sometimes when the machine is turned off the 2A fuse in the neutral will blow.
Anyone come across this before?
IF
the switch is double pole and
the switch is turning off stuff other than the PLC PSU and
the switch happens to sometimes break neutral before live and
there is a neutral to earth fault in the PLC PSU
then it would explain the neutral fuse to the PLC PSU blowing.
That is the only explanation I could come up with for why it's always the neutral fuse...
When the Italians design electrics this happens!
Draw your own conclusions :p
Two possible causes
[1] current flowing in or out of the filter capacitor between neutral and earth / ground as the PSU shuts down. Neutral and earth being connected together in the mains supply network means there is a circuit for the capacitors to discharge
If there is pre-regulator in the PSU ( 300 + volts DC ) then this may dump via the neutral when the mains live is removed and the regulator is shutting down the outputs in a controlled way.
[2] The neutral in the PSU is connected to or has a low impedance path to the 0 volt of the field wiring thus creating a low impedance path between supply neutral and earth / ground. This could be intentional or a wring fault which does not noticably affect operation of the equipment. That connection would then be a route for current from a potential on the neutral of an un-balanced 3 phase supply to ground.