The loop impedance to trip within permitted time should be less than 1.38Ω and to be within volt drop approx no more than 0.63Ω over the incoming line - neutral reading. So line - earth better than 1.38Ω and line - neutral better than 0.98Ω better means less than.
By inquiry is valid, so you can get the original installation certificate and simply add on the impedance of the extra circuit. A ring final can have up to 106 meters of cable, and it is unlikely that is exceeded, and to be frank even if the permitted 5% for sockets is exceeded it is unlikely to cause a problem, same with the 3% volt drop allowed for lighting.
Two work, and to comply with regulations, is not the same. And with RCD protection, 200Ω is considered the limit, after that it is seen as being unstable. And some of the rules are rather antiquated, the 3% volt drop limit for lights was because a wire wound ballast on a fluorescent light was very voltage dependent, 30 volts can make the difference between using twice the rated current and not striking, and we used to have auto switching auto transformers to reduce the power used, today they are seen as snake oil.
However, as an electrician without getting my meters out of their box, I can look at an installation and have a reasonably good idea as to how close to the wind I am sailing. Not quite so easy for the DIY guy, so the loop impedance permitted with a 13 amp fuse, is around 2.42Ω, which is a lot higher than the 1.38Ω (was 1.44Ω) allowed for a B32 MCB/RCBO. So assuming the original installation was compliant, then the 13 amp FCU as I showed is also likely compliant, but to extend the ring final, you either need a loop impedance meter to measure, or a low ohm meter to measure, or the readings from the installation certificate before you started to alter it.
With a 2 up 2 down property unlikely to be a problem, with a 6-bedroom house, then likely you need the readings.