With new modern boilers I aim for 0.002 co/co2 ratio, some achieve 0.001.
Gritish Bas guidelines are commonly accepted (stated in the Corgi manual actually) in the UK which are that 0.004 is a soft target and 0.008 is a hard target. That means that if it is between the two you should investigate. It is also accepted that after debris has been stirred up through maintenance temporarily the reading may be 0.008 and this is acceptable.
This practise corresponds to about 500ppm CO inside the flue gases (not by adjusted free air test).
So what we are saying is that CO of 500ppm inside the flue is worth investigating.
The Italians who use the absolute CO value as their guide method accept 1,000 ppm CO.
To put this in perspective, a band D combi with a boarderline fan performance such that the aps is flaging up a fualt intermittently, say where the fan pressure is 0.4 instead of 1mBar, would probably still be working at between 50 to 500 ppm CO or 0.004 to 0.008 ratio.
Now a boiler with fan in this condition I would consider delapi#dated and in gross need of attention.
Interesting to note in the light of recent events that the Italians would be fairly happy with a spider waiving a triangle shaped piece of paper in the flue!
Comments?
Gritish Bas guidelines are commonly accepted (stated in the Corgi manual actually) in the UK which are that 0.004 is a soft target and 0.008 is a hard target. That means that if it is between the two you should investigate. It is also accepted that after debris has been stirred up through maintenance temporarily the reading may be 0.008 and this is acceptable.
This practise corresponds to about 500ppm CO inside the flue gases (not by adjusted free air test).
So what we are saying is that CO of 500ppm inside the flue is worth investigating.
The Italians who use the absolute CO value as their guide method accept 1,000 ppm CO.
To put this in perspective, a band D combi with a boarderline fan performance such that the aps is flaging up a fualt intermittently, say where the fan pressure is 0.4 instead of 1mBar, would probably still be working at between 50 to 500 ppm CO or 0.004 to 0.008 ratio.
Now a boiler with fan in this condition I would consider delapi#dated and in gross need of attention.
Interesting to note in the light of recent events that the Italians would be fairly happy with a spider waiving a triangle shaped piece of paper in the flue!
Comments?