Gas pipe size
13 Oct 2003
I am installing a new combi boiler rated at 39.6 Kw (135115 BTU/hr) gross input. This will be fed through 10.5 m of gas pipe with a gas cooker and hob teeing off after 6m. Are there any Corgis out there who can advise whether I should be going for 28mm pipe for all or some of the run? I will be getting a Corgi to connect to the supply and commision but want to get the work done on the piping. :confused:
have you already found someone who will connect the boiler and commission to your new pipework because i don't know many corgis who will take on somebody elses installation and put their name to it. You would need the kw of the cooker/hob and add 0.5m for every tee or elbow to work out the pipe size.
No, not tried to find someone yet - good point.
Don't know oven size yet, hob will be 8 to 9Kw I think.
Agree with Ollski
The gas saftey installation and use regs state that any pipe that is intended to convey gas must be installed by a competent person
I for one would never entertain "commisioning" a pipe for gas that has been installed by a non registered plumber let alone a client
spend a bit of cash and get a corgi op to install it for you peace of mind comes at a cost
FWIW, You will need 28mm from the meter to the tee, 22mm from the tee to the boiler and probably (depending on size of cooker and hob) 22mm from tee to cooker and hob tee, posssiby reducing to 15mm from there to appliances.