After reading a recent thread about undersized gas pipework and the dangers of it, I decided to inspect my system - which was installed by the previous owner of my house about 3 years ago (who was an RGI, but still a bit of a cowboy.)
First thing I noticed was all the gas piping is in 15mm. My boiler is a 24kW combi that is located in a cupboard right next to the gas meter. The pipework from the meter to the boiler is less than 1m in length, and there is a t-piece half way along, leading under the floor to the gas hobs (oven is electric.)
I thought I'd do a little bit of an acid test last night to see what would happen if I had all the hobs running at full, and I fired the boiler up on full DWH demand. So I tried it and what I saw was the flames on the hobs 'blip' a little bit as the gas valve opened, then very slightly blip again as the boiler goes off.
Could anyone tell me whether this behaviour is normal? The manual states the boiler only needs a 15mm connection, but I'm thinking what should have been done is 22mm piping from the meter and to the hobs, then a t-piece with 15mm reducer to the boiler. The reason I'm asking you guys is I'm wanting to install a small gas fire in the front room, and want to prepare myself with the additional money if the pipework needs upgrading.
I understand that the gas pressure will have to be checked anyway, but I just wonder whether the blipping is a sure sign that the pressure drop is too high.
First thing I noticed was all the gas piping is in 15mm. My boiler is a 24kW combi that is located in a cupboard right next to the gas meter. The pipework from the meter to the boiler is less than 1m in length, and there is a t-piece half way along, leading under the floor to the gas hobs (oven is electric.)
I thought I'd do a little bit of an acid test last night to see what would happen if I had all the hobs running at full, and I fired the boiler up on full DWH demand. So I tried it and what I saw was the flames on the hobs 'blip' a little bit as the gas valve opened, then very slightly blip again as the boiler goes off.
Could anyone tell me whether this behaviour is normal? The manual states the boiler only needs a 15mm connection, but I'm thinking what should have been done is 22mm piping from the meter and to the hobs, then a t-piece with 15mm reducer to the boiler. The reason I'm asking you guys is I'm wanting to install a small gas fire in the front room, and want to prepare myself with the additional money if the pipework needs upgrading.
I understand that the gas pressure will have to be checked anyway, but I just wonder whether the blipping is a sure sign that the pressure drop is too high.