Just checked the Gas Rate on my boilers in a) House and b) Annex. The House is a System Boiler and Annex is a Combi,
I've checked them both on CH over 120 sec, and I know I need to do the Combi with HW demand rather than CH, but came out with a high value on the Combi CH so I'm booking in a service.
The results are:
House (System Boiler) - Vaillant ecoTEC plus 630 (30kw)
- 6.01kw Gross
Annex (Combi) albeit set to CH demand for Gas rate test. - Vaillant TURBOmax Plus 828 E - (28kW)
- 20.17kW Gross
In both cases I did a few Gas Rate samples, but have taken the average of each boiler for the above.
The House Boiler definitely modulates and to be fair, had been on so return flow was already pretty high, and I think I recall the display showing a high modulation on the bar graph.
The Annex - TURBOmax 828, is not very sophisticated and does not give any feedback on modulation level. Equally, I think that boiler modulates after 2 min or so , so would not apply within the first 2min of gas rate test. Either way, it seems the 1 room, 3 rad Annex is a lot higher than my house that is much bigger.
I'll be informing the Gas eng of what my observations are, so he definitely checks the gas rate in the service, but I'm wondering if anybody would be concerned with the Annex Combi Gas Rate of 20kw with CH demand ? perhaps I'm being over cautious, but don’t want to be burning extra gas or ignoring a problem, so thought its worth having an additional service call even if its not due.
I've checked them both on CH over 120 sec, and I know I need to do the Combi with HW demand rather than CH, but came out with a high value on the Combi CH so I'm booking in a service.
The results are:
House (System Boiler) - Vaillant ecoTEC plus 630 (30kw)
- 6.01kw Gross
Annex (Combi) albeit set to CH demand for Gas rate test. - Vaillant TURBOmax Plus 828 E - (28kW)
- 20.17kW Gross
In both cases I did a few Gas Rate samples, but have taken the average of each boiler for the above.
The House Boiler definitely modulates and to be fair, had been on so return flow was already pretty high, and I think I recall the display showing a high modulation on the bar graph.
The Annex - TURBOmax 828, is not very sophisticated and does not give any feedback on modulation level. Equally, I think that boiler modulates after 2 min or so , so would not apply within the first 2min of gas rate test. Either way, it seems the 1 room, 3 rad Annex is a lot higher than my house that is much bigger.
I'll be informing the Gas eng of what my observations are, so he definitely checks the gas rate in the service, but I'm wondering if anybody would be concerned with the Annex Combi Gas Rate of 20kw with CH demand ? perhaps I'm being over cautious, but don’t want to be burning extra gas or ignoring a problem, so thought its worth having an additional service call even if its not due.