What ho one and all,
First a bit of background.
I own a maisonette, current rented out, which has a Potterton Kingfisher boiler. It regularly passes its annual Gas Safe test, usually with what appears to be flying colours.
On Dec 24, the tenant phoned in panic as the CO alarm had activated. She turned the incoming gas off and called the emergency gas people, who arrived and disconnected the boiler. I swung by a very local gas engineering company and they had a free engineer who came immediately and ran some tests. He found that the flue gas was registering 0ppm so figured that the alarm (or its batteries) was at fault. I replaced the alarm and all was fine.
He offered to fill out a Gas Safe certificate as the new one was due mid Jan 2016, but as I had already booked and pre-paid someone to do this, I declined.
Jan 4, the Gas Safe guy came and found that the flue gas reading was around 500 - 600 ppm and closed the boiler down. This guy is not an 'engineer' as such, but from a franchise (company) who specialise in testing domestic gas equipment but not servicing.
Anyway, I went back to the Dec 24 company and had a whinge; the same engineer was free so returned to have a look and service the boiler. This time, he found a flue gas reading of about the same (500ppm). During the service, the only fault he could find was an excess of dust around the fine air intake filter mesh. There was no flue blockage and no flue gas leaking anywhere. Post cleaning flue gas readings came in at 11 - 14 ppm, so he issued the annual pass certificate.
He had brought his meter and a newer version to double check but was unable to use the newer one as it had a different interface and this probe would not fit.
I am now querying the invoice for the first visit, since he could have issued a pass certificate when it subsequently appears that the boiler was giving excess CO. The company are of course not happy!
Given that the certificate is really only good at the time of the reading, how likely is it that a boiler can go from 0ppm to 500 ppm in 10 days? How likely is it that an old style boiler can be giving a reading of 0ppm? If he had issued a certificate on Dec 24 and subsequently there was a medical problem due to excess CO (the tenants have a small child!), who would be responsible since I would have fulfilled the legal obligations?
I will be happy to pay the servicing and certificate issue fee, but at the moment, not the Dec24. / CO alarm ringing / 0ppm reading check fee. Where do I stand?
Many thanks for reading all this.
Rex
First a bit of background.
I own a maisonette, current rented out, which has a Potterton Kingfisher boiler. It regularly passes its annual Gas Safe test, usually with what appears to be flying colours.
On Dec 24, the tenant phoned in panic as the CO alarm had activated. She turned the incoming gas off and called the emergency gas people, who arrived and disconnected the boiler. I swung by a very local gas engineering company and they had a free engineer who came immediately and ran some tests. He found that the flue gas was registering 0ppm so figured that the alarm (or its batteries) was at fault. I replaced the alarm and all was fine.
He offered to fill out a Gas Safe certificate as the new one was due mid Jan 2016, but as I had already booked and pre-paid someone to do this, I declined.
Jan 4, the Gas Safe guy came and found that the flue gas reading was around 500 - 600 ppm and closed the boiler down. This guy is not an 'engineer' as such, but from a franchise (company) who specialise in testing domestic gas equipment but not servicing.
Anyway, I went back to the Dec 24 company and had a whinge; the same engineer was free so returned to have a look and service the boiler. This time, he found a flue gas reading of about the same (500ppm). During the service, the only fault he could find was an excess of dust around the fine air intake filter mesh. There was no flue blockage and no flue gas leaking anywhere. Post cleaning flue gas readings came in at 11 - 14 ppm, so he issued the annual pass certificate.
He had brought his meter and a newer version to double check but was unable to use the newer one as it had a different interface and this probe would not fit.
I am now querying the invoice for the first visit, since he could have issued a pass certificate when it subsequently appears that the boiler was giving excess CO. The company are of course not happy!
Given that the certificate is really only good at the time of the reading, how likely is it that a boiler can go from 0ppm to 500 ppm in 10 days? How likely is it that an old style boiler can be giving a reading of 0ppm? If he had issued a certificate on Dec 24 and subsequently there was a medical problem due to excess CO (the tenants have a small child!), who would be responsible since I would have fulfilled the legal obligations?
I will be happy to pay the servicing and certificate issue fee, but at the moment, not the Dec24. / CO alarm ringing / 0ppm reading check fee. Where do I stand?
Many thanks for reading all this.
Rex