My Baxi Platinum 28 HE (47-075-21) has had the following fitted. Refurbished main heat exchanger, refurbished PCB, new electrodes and a second new gas valve. The boiler is back up and running but the gas goes off as it gets near the temperature the central heating has been set to and then the gas repeatedly goes on and off until the boiler gets to the set temperature and then the gas goes off until the temperature has dropped enough for the boiler to fire up again. The cycle repeats continuously until the thermostat in the living room turns the boiler off.
My GAS SAFE REGISTERED ENGINEER thought it could be a faulty CH NTC sensor but if I turn the hot water to the lowest setting I get the same problem.
I cannot remember what he set the high to apart from the fact it was within 8.7 +/-0.2 however the low is 8.3 which is on the low side but within tolerance 8.4 +/- 0.2. Before I get my GAS SAFE REGISTERED ENGINEER back and have him set it to 8.5 or even 8.6 which will hopefully sort out the problem does anyone know if there is anything else that could cause the same problem?
My GAS SAFE REGISTERED ENGINEER thought it could be a faulty CH NTC sensor but if I turn the hot water to the lowest setting I get the same problem.
I cannot remember what he set the high to apart from the fact it was within 8.7 +/-0.2 however the low is 8.3 which is on the low side but within tolerance 8.4 +/- 0.2. Before I get my GAS SAFE REGISTERED ENGINEER back and have him set it to 8.5 or even 8.6 which will hopefully sort out the problem does anyone know if there is anything else that could cause the same problem?