Finally had BG out to do the annual service on our boiler which we didn't get last year. We had the check booked in but it was cancelled twice by BG at the last minute due to other demands through the covid situation. The boiler was found to have a problem when it was checked yesterday.
I gather there is a threshold of 10PPM of CO, and the engineer was picking up 12PPM, and a fair bit of corrosion on the brackets holding the main heat exchanger and in the base of the boiler case, so his diagnosis is the plastic flue adapter is leaking. So it is out of action at the moment. We do have a CO alarm near to it and that wasn't picking anything up, but that's possible given the boiler is in our (integral to the house) garage.
I've had a look myself with a tiny USB camera I have, and initial impression was quite bad - i.e. it looks like rampant crusty rot in the areas where the condensate had leaked out, but when I take a little wire brush to it, it cleans back to smooth surface rust. So it looks to me like the condensate has attacked and lifted the galvanised coating on the brackets etc. such that it looks far worse than it actually is. That being said, some of that rust is on the brackets very close to the body of the main heat exchanger and whilst I can't see any clear damage to the rear or seams of the heat exchanger itself, that remains a possibility and I imagine will write the boiler off if that has occurred. The photo below shows the one suspicious looking area on the rear seam near to one of the corroded brackets. I guess the dilemma is whether the CO levels are due to the flue adapter and its leak, or whether it's due to damage to the heat exchanger.
I'm being given the option of the repair being attempted as it's under maintenance (that looks an awkward repair that will involve the main heat exchanger having to come out), OR a few hundred extra discount on a new boiler to offset the repair if they don't attempt it, and further discounts on the mtce to take account of the warranty. The boiler was installed in 2004 and hasn't given any problems till now, but at 17 years old, it is beyond the 10-15 years life expectancy often quoted these days.
So I'm just edging towards replacement right now (whether by BG or someone else) but would value any thoughts.
Thanks.
I gather there is a threshold of 10PPM of CO, and the engineer was picking up 12PPM, and a fair bit of corrosion on the brackets holding the main heat exchanger and in the base of the boiler case, so his diagnosis is the plastic flue adapter is leaking. So it is out of action at the moment. We do have a CO alarm near to it and that wasn't picking anything up, but that's possible given the boiler is in our (integral to the house) garage.
I've had a look myself with a tiny USB camera I have, and initial impression was quite bad - i.e. it looks like rampant crusty rot in the areas where the condensate had leaked out, but when I take a little wire brush to it, it cleans back to smooth surface rust. So it looks to me like the condensate has attacked and lifted the galvanised coating on the brackets etc. such that it looks far worse than it actually is. That being said, some of that rust is on the brackets very close to the body of the main heat exchanger and whilst I can't see any clear damage to the rear or seams of the heat exchanger itself, that remains a possibility and I imagine will write the boiler off if that has occurred. The photo below shows the one suspicious looking area on the rear seam near to one of the corroded brackets. I guess the dilemma is whether the CO levels are due to the flue adapter and its leak, or whether it's due to damage to the heat exchanger.
I'm being given the option of the repair being attempted as it's under maintenance (that looks an awkward repair that will involve the main heat exchanger having to come out), OR a few hundred extra discount on a new boiler to offset the repair if they don't attempt it, and further discounts on the mtce to take account of the warranty. The boiler was installed in 2004 and hasn't given any problems till now, but at 17 years old, it is beyond the 10-15 years life expectancy often quoted these days.
So I'm just edging towards replacement right now (whether by BG or someone else) but would value any thoughts.
Thanks.