The short version...
Glow Worm 23C boiler is repeatedly losing pressure (red warning light flashes, and pressure reading on the LED flashes). Opening the filling tap re-pressurises the system, but I have to do this repeatedly (pretty much every time I leave the heating / hot water unused for more than a couple of hours!)
The long version...
I've had problems with the boiler for a while. It's the same boiler that was here when I moved in, and it's always had occasional problems with low pressure, which tended to be resolved by opening the filling tap as instructed in the manual. However, the pressure reading never went very high even when the system was hot, and opening the filling tap pretty much always resulted in water leaking out from under the boiler (even when the boiler was indicating low pressure!)
Around Xmas time I had some more critical problems, the boiler wouldn't fire at all, the error light was constantly flashing. Luckily I have emergency boiler cover, and someone came, found it was the overheat sensor tripped, and reset. This happened again a few weeks later, and was reset again. The engineer set the central heating temperature on the boiler slightly lower (3/5 rather than 5/5) in the hope of stopping it happening again, and recommended a powerflush (because radiators were slightly cooler at the bottom than the top - but didn't seem to give any reasoning why this might help the overheating problem). I haven't had a powerflush, and it hasn't overheated again since...
The blue filling valve then broke off entirely (it's only clipped on by a few flimsy plastic bits), so the filling valve got replaced - while the engineer was doing this, he found the pressure sensor in the boiler wasn't working correctly, so this was also replaced. Engineer also explained this was probably why I was getting low pressure faults, but then water would leak out of the boiler when the filling tap was open. I thought, great, hopefully this will fix all my problems!
Unfortunately not. Now the system seems to work fine when the heating or hot water are on, but when nothing is on (ie. middle of the night or when I'm at work) the system loses pressure and I have to re-pressurise. This means I'm effectively having to re-pressurise by opening the filling tap twice a day! Every morning so I can have a hot shower, and every evening when I get in from work so I can have some central heating!
The pressure sensor appears to be working now. I've seen it go up to about 1.5, which I'd pretty much never seen before, and when it reports low pressure and I open the filling valve I don't immediately get water leaking out implying it's already correctly pressurised. Instead I hear water filling for a short period, and then the error clears, but it's very frustrating having to do this twice a day, and I'm concerned this implies a wider problem. I can't see any evidence of leaking radiators, or that the boiler is leaking...
Any advice on how to get to the root of the problem? Does anyone think the powerflush might be useful?
Thanks[/b]
Glow Worm 23C boiler is repeatedly losing pressure (red warning light flashes, and pressure reading on the LED flashes). Opening the filling tap re-pressurises the system, but I have to do this repeatedly (pretty much every time I leave the heating / hot water unused for more than a couple of hours!)
The long version...
I've had problems with the boiler for a while. It's the same boiler that was here when I moved in, and it's always had occasional problems with low pressure, which tended to be resolved by opening the filling tap as instructed in the manual. However, the pressure reading never went very high even when the system was hot, and opening the filling tap pretty much always resulted in water leaking out from under the boiler (even when the boiler was indicating low pressure!)
Around Xmas time I had some more critical problems, the boiler wouldn't fire at all, the error light was constantly flashing. Luckily I have emergency boiler cover, and someone came, found it was the overheat sensor tripped, and reset. This happened again a few weeks later, and was reset again. The engineer set the central heating temperature on the boiler slightly lower (3/5 rather than 5/5) in the hope of stopping it happening again, and recommended a powerflush (because radiators were slightly cooler at the bottom than the top - but didn't seem to give any reasoning why this might help the overheating problem). I haven't had a powerflush, and it hasn't overheated again since...
The blue filling valve then broke off entirely (it's only clipped on by a few flimsy plastic bits), so the filling valve got replaced - while the engineer was doing this, he found the pressure sensor in the boiler wasn't working correctly, so this was also replaced. Engineer also explained this was probably why I was getting low pressure faults, but then water would leak out of the boiler when the filling tap was open. I thought, great, hopefully this will fix all my problems!
Unfortunately not. Now the system seems to work fine when the heating or hot water are on, but when nothing is on (ie. middle of the night or when I'm at work) the system loses pressure and I have to re-pressurise. This means I'm effectively having to re-pressurise by opening the filling tap twice a day! Every morning so I can have a hot shower, and every evening when I get in from work so I can have some central heating!
The pressure sensor appears to be working now. I've seen it go up to about 1.5, which I'd pretty much never seen before, and when it reports low pressure and I open the filling valve I don't immediately get water leaking out implying it's already correctly pressurised. Instead I hear water filling for a short period, and then the error clears, but it's very frustrating having to do this twice a day, and I'm concerned this implies a wider problem. I can't see any evidence of leaking radiators, or that the boiler is leaking...
Any advice on how to get to the root of the problem? Does anyone think the powerflush might be useful?
Thanks[/b]