Hi All.
Just back from looking at a 18hxi ( customer says that he'd posted the problems with it on this forum and TOLD me to reset the O/H stat).
It was stuck on F5 - fair do's. Told me he'd been also having probs with the boiler showing the F1 - ignition fault for months, and that the electrode had been replaced.
Took the cover off and took a look. Firstly, noticed that the electrode earth lead was charred around the spade connector. Then also noticed scorching (on the insulation that sits on the side panel), at the side of the burner. Obviously the burner gets hot, but not to the point of scorching??. The 3 nuts on that right side of the burner were only finger tight!!
I imagine the burner seals have perished as a result of this allowing excess heat to leak onto that side. Must also account for all those F1 ignition faults. I'm sure these seals have been upgraded to ? graphite. Anyone have the code or GC No to hand, or know whre i can get replacements asap.
undercover
Just back from looking at a 18hxi ( customer says that he'd posted the problems with it on this forum and TOLD me to reset the O/H stat).
It was stuck on F5 - fair do's. Told me he'd been also having probs with the boiler showing the F1 - ignition fault for months, and that the electrode had been replaced.
Took the cover off and took a look. Firstly, noticed that the electrode earth lead was charred around the spade connector. Then also noticed scorching (on the insulation that sits on the side panel), at the side of the burner. Obviously the burner gets hot, but not to the point of scorching??. The 3 nuts on that right side of the burner were only finger tight!!
I imagine the burner seals have perished as a result of this allowing excess heat to leak onto that side. Must also account for all those F1 ignition faults. I'm sure these seals have been upgraded to ? graphite. Anyone have the code or GC No to hand, or know whre i can get replacements asap.
undercover