glowworm ultimate 40ff

Joined
19 Sep 2007
Messages
47
Reaction score
0
Location
Manchester
Country
United Kingdom
hi i have a glowworm ultimate 40ff, and havin problems lightin up, fan starts up, and 2 lights appear on circuit board, but then its starts clickin as though somethin is stoppin the next procedure, changed aps but still the same, can anyone help please
cheers
 
Sponsored Links
Check for voltage at the gas valve, look in MI's. If present, sounds like gas valve knackered.

Edit; does this have a pilot that is lit first electronically? If so could be pilot injector blocked.

Corgi job though.
 
yes its electnic ignition, and cleaned that, wat MIs, it did work for a bit then goes off and does wat its doin and its stayed like that since
 
Gas valve has twin solenoids check for 240 at connections if there is swap them over if the pilot then lights and no main burner you then know it needs a new solenoid.

If APS was faulty it would not get as far as sparking.
 
Sponsored Links
i have the same boiler with the same problem when switched on and light the pilot through the view hole evreything work as normal until you switch it of again
 