Gravity fed problems. Hot water on only - Radiators hot

Joined
4 Mar 2007
Messages
4
Reaction score
0
Location
Bristol
Country
United Kingdom
Hi
I have a 15 year old gravity fed system. When i put on the hot water only, the radiators get very hot and the hot water gets used up. I had both the radiators on and the hot water on and the house got very hot. i turned the room thermostat down to 10c but the radiators stayed very hot.

Please help

Thanks

Glenn
 
Sponsored Links
On the heating flow pipe there should be an anti gravity valve it is usually within a few feet of boiler, looks like a brass socket . This is sticking and allowing water around heating circuit. Needs changing
 
or tapping with a Brummie screwdriver..(hammer) ;)
 
is it all the rads or just upstairs ones, if so get ya brummie screwdriver to hand
 
Sponsored Links
oh yeh
forgot to say
The system is gravity fed but is a fully pumped system.
Does this make a difference??
Somebody mentioned to me could be wired up wrong??
Thanks
 
wired up wrong ide say either that or your control valve is letting heat by/stuck open, it will be a three port or 2x two ports
 
If this problem has only occured recently and no work has been carried out on the system recently then a 2-port or 3-port valve is probably faulty.
If the system has been doing it for 15 years then the system is wired up wrong or piped up wrong.
 
Nige F said:
or tapping with a Brummie screwdriver..(hammer) ;)

Or your apprentice when youve had a day like mine with him (or her)

David
 
Most old systems on gravity would have the roomstat contoling the pump directly
 