This is probably easily understandable to someone but has got me completely stumped!
The Pressure gauge is dropping about 0.1 bar everytime the radiator burner/pump kicks in. If I put the heating on it goes down from 1 bar to zero in about 2-3 hours. (constantly dropping 0.1 bar everytime the burner kicks in until reaches zero).
If I pressurise the system to 2 bar and leave overnight without use, it is still two bar in the morning (so I am pretty confident its not the rads/pipes)
I have also noticed that when the hot water is turned on, the pressure will drop 0.25 bar while the hot water is running before returning back to previous presure reading when the hot water is turned off.
I have also noticed that the hot water still works even though the presure gauge is reading zero (I thought there was supposed to be a complete system cutoff when the presure drops too low?)
Cannot find a leak anywhere... including around the boiler area or external pressure relief pipe. I cannot easily monitor the condensation pipe due to the way that it has been plumbed in.
Any idea whats going on?
Any pointers much appriciated.
This is probably easily understandable to someone but has got me completely stumped!
The Pressure gauge is dropping about 0.1 bar everytime the radiator burner/pump kicks in. If I put the heating on it goes down from 1 bar to zero in about 2-3 hours. (constantly dropping 0.1 bar everytime the burner kicks in until reaches zero).
If I pressurise the system to 2 bar and leave overnight without use, it is still two bar in the morning (so I am pretty confident its not the rads/pipes)
I have also noticed that when the hot water is turned on, the pressure will drop 0.25 bar while the hot water is running before returning back to previous presure reading when the hot water is turned off.
I have also noticed that the hot water still works even though the presure gauge is reading zero (I thought there was supposed to be a complete system cutoff when the presure drops too low?)
Cannot find a leak anywhere... including around the boiler area or external pressure relief pipe. I cannot easily monitor the condensation pipe due to the way that it has been plumbed in.
Any idea whats going on?
Any pointers much appriciated.