Hi All,
Current Normal Pressure = 1.5 (hasn't been topped up for months)
Just Hot Water being used - pressure remains at 1.5
Just C/H on, the pressure quickly rises to just over 3
Pressure doesn't drop below 1.5 (which is where mine differs from other posts as others seems to drop to zero and stop working).
Checked pressure vessel and no water comes out when pin pressed in
Checked pressure relief overflow pipe (ie copper pipe) and no dripping or water escaping (cobwebs are still inside)
C/H and H/W works fine everytime. Pressure increase only noticed the last few weeks and was serviced only a few months ago and every year since new (approx 11 years old now).
Could this still be the pressure vessel not having enough air in? (haven't checked actual pressure in tbh). or something else?
Thanks