I've got an odd problem in that my grundfos 15/50 central heating pump gets noisy but only when boiler switches off and its on overun. Is the pump on its way out or is there something else wrong?

Pete
 
Sponsored Links
It could be that you have no Bypass valve on the system and when your motorised valve closes the pump isnt moving any water and cavitates producing noise.do you have 2 seperate zone valves or one three port valve.
 
is there a by-pass that is actually allowing water through?
 
i have 2 motorised valves... i assume one for heating and one for hot water.... its not a problem that i've always had... its stated recently.
 
Sponsored Links
oh... and stops making a noise if i turn it down to speed 1 during overun.... i once got rid of noise by momentarily turning it up to 3 and then back to 2. It came back though.
 
i have seen a bypass and its open.... i can only asume its letting water through...
 
You could do better than assume, you could see if the pipework either side of the bypass is the same (hot) temperature
 
ok... i'll check that in the morning and get back to you. thanks for your input.
 
Sorry about the delay... so ... the bypass valve seems to be working ok... pipes hot either side...
 
Thanks Guys....
I tweaked the bypass valve a little until the noise stopped. System still working fine so i guess its fixed. Why might it have started playing up in the first place?
 