Today I visited a property.

The customer was complaining of voltage drop when a hefty appliance was used on the ground floor ring final.

He said that fluorescent lights would dim & appliances with motors would slow down.

I plugged my trusty Alphatek into the cooker control unit & it read 237V. Fair enough.

Then I asked the customer to plug a kettle into the GF RF & switch on.

Sure enough, the voltage plummeted to 199V.

What fault did I find?

;)
 
Sponsored Links
Sponsored Links
aA 100kw Kettle with a 15,000litre capacity (big tea drinkers living downstairs) :LOL:
 
What I actually found was two problems.

There's a bit of a clue....
 
Two loose tails? :LOL:

OK - maybe the sockets were wired off the lighting circuit and had a solid metal link in instead of a fuse?
 
I'm thinking some weird F'ed up polarity reversal plus neutral fault somewhere that we'd never guess in a billion years.

I had a feeling this would be a double, the best ones always are.
 
N>E fault on kettle

L&N reversed at incommer

Zs 3.29 ohms at the socket
 
Problem with tails connection into main switch or main switch on to busbar/outgoing N link?? (wrong side of clamp/s)
 