I've had problems with the pressure dropping in my system when the CH is running. Pressure remains constant with no heating on. Set it to about 1.5. After heating has been on, and cooled down again pressure has often dropped below one. Halstead suggested either that the pressure vessel may need repressurizing with more air or a faulty pressure relief valve. My money is on the PRV since when pressure gets to about 2.5 max (but only once in a while - usually stable at around 2 when CH is running) you get some venting of water from the system - pressure has never reached 3 which is what the valve is rated at. Plumber (good mate and honest guy) thought vessel might need topping up with air as well based on what Halstead had suggested. Anyway he managed to vent air from vessel rather than topping it up (!) and then wasn't too sure what air pressure it needed to be topped up to so guessed (!!). It was air that came out and not water suggesting the diaphragm is intact. Also cleaned out the PRV. Seemed to work OK, but now I'm getting water venting again as before. So a) do you reckon it's a problem with the PRV which needs replacing b) would a pressure vessel fault look like this c) what air pressure should the vessel have been topped up to and can you use the guage on the bolier to measure this or do you need a separate guage?
Cheers - Frazz