Halstead Ace pressure

Joined
25 Oct 2008
Messages
13
Reaction score
0
Location
Derbyshire
Country
United Kingdom
Recently had a new pcb board fitted on Halstead Ace boiler. The boiler kept to a constant pressure before this. Since this was fitted the central heating pressure rises up to about 2 bar and would continue to rise if i let it. The pressure rise is very slow over about an 8 hour period when the central heating is on. When I get up in the morning after the heating has been off the guage is only just under 2 bar so i ive been draining water off to drop it back down to about 1bar. i then go through the above process the following day. I just dont want anything to go wrong over the christmas period anyone any ideas what the problem could be thanks
 
Sponsored Links
completley remove braided hose from filling loop to eliminate possible passing valve
 