Halstead Quattro Propane Combination Boiler

Joined
13 Aug 2007
Messages
2
Reaction score
0
Location
London
Country
United Kingdom
The DHW supply has had an intermittent fault, where the water would run cold after a while (especially if the demand was low) but it could usually be reset by turning the hot tap off and back on again.

The fault has now worsened and the burner will not fire up at all on DHW demand, however hot water is available if the CH is turned on at the same time.

Any ideas?
 
Sponsored Links
Pook said:


The DHW supply has had an intermittent fault, where the water would run cold after a while (especially if the demand was low) but it could usually be reset by turning the hot tap off and back on again.

The fault has now worsened and the burner will not fire up at all on DHW demand, however hot water is available if the CH is turned on at the same time.

Any ideas?


Bothering to look at Forum Etiquette may be a start.
 
FIrst thing to look at would be the diaphragm.

do a search on that and quattro
 
Bambergaspipe said:
Bothering to look at Forum Etiquette may be a start.

So I am now compliant with rule 6a, have got any intelligent input Bambergaspipe? Having looked at your other posts, I guess not!
 
Sponsored Links
As suggested its most likely to be the diverter valve failed but there are several possibilities apart from the diaphragm unit although thats the most common.

Tony
 