i have a heat line boiler every time i run water pilot stays on for abt 20 sec goes off then reignites :confused:
 
Sponsored Links
All the H-L boilers I can think of use a turbine flow sensor with Hall effect detector. They cannot stay activated without water flow.

See if turning off DHW flow or monitor the Hall effect detector with a scope.

Tony
 