I have an open vented system with a conventional boiler. Moved in recently and two heated towel rails came on with both heating and hot water. After a couple of weeks one towel rail has stopped coming on with the hot water. It still works fine when the heating is on! Any ideas?

Cheers
 
Sponsored Links
Nothing altered anywhere in the system to my knowledge. Valves on affected towel rail are open.
 
Have you bled the towel rail - and check the f+e cistern water
 
Sponsored Links
Towel rails and other rads all bled. Will check the F+E tank, thanks!
 