Can any one HELP? The Radiators Fail to come on when switched on at the control box. The Hot Water Will come on however. I have traced the fault - their are two Honeywell V4043 Motorised Zone Valves, on the pipes out of the Oil fueled boiler. One is I assume the Hot Water which is Working, the other must be the Heating. I pushed the switch on the V4043 from Auto to Manual Open, and Radiators started to heatup, at the same time I kept the HotWater ON, so the Pump was running. DO I need to just buy a new V4043 (I think it is the Normally Closed Type valve)? Does this valve also switch on the boiler and pump, because if I switch off the HotWater, then the pump stops, hence just opening the Heating Valve to Manual, will not in its self start the pump etc, if I have the HotWater switched Off. Am I on the right tracks, or could there be an electrical fault of some sort instead?
Any Comments much appreciated!
Richard.