Heating on all the time

Joined
3 Dec 2011
Messages
28
Reaction score
0
Location
Edinburgh
Country
United Kingdom
My system is
valiant ectoc plus 428
unistor 310
vr 65
vrt 360 f
I have tried to get a Central heating engineer out, unfortunately, none able to come for weeks.
The issue is, the boiler shows that radiators are calling for heat even when the thermostat isn't.
Changed the 3 way valve, same make and wired the same, no improvement, the Led in the VR 65 is green.
Hot water is fine, will on go on when set to come on. On way to switch of the heat is to switch the powerswitch on the VR 65. TIA
 
Sponsored Links
Has it always done it, or is it more recently?
 
It has only done it over the last few weeks. Previously had an issue about 5 years ago, put a new 3 way valve,fixed the issue.
 
Sounds like a stuck relay in the vr65, turn the power off and open the front of the vr65, you will see a row of relays just gently tap the tops and see if the ch relay frees its self.
 
Sponsored Links
I will give it ago, other thing I noticed, Even now when I switch on thevrt 65 to off, boiler is still has the radiator demand on boiler display.
 
Tried taping the relays, unfortunately still the same. I did suspect the vrt 65, but reluctant to replace it as I had thought of a complete new system later in the year. This system is 14 years old
 
Not keen about replacing the vrt65, but I see it's not available now. I presume the vrt 66 is a replacement with 2 heating zones than the 1 with the vrt 65. I would probably have to replace the vrt360, as it doesn't look its compatible with the newer vr 66, any advice would be great.
 
The original heating engineer fitted a 3 port at the time of installation, been replaced with same type about 5 years ago.
 
Not what I asked o_O I there a two port valve fitted on the unvented cylinder flow ?
 
No, central heating engineer never fitted one at the time of installation to the hot water, 3 port valve fitted at the time.
 
Just checked the voltage on the 3 port connections at the vr65, when the vrt360 isn't set for heating or hot water, both the hot water on and off are reading 240, heating live is 240, but boiler not active. If I switch the power off to central heating completely and back on, the boiler comes on, connections still show 240v. Looks like vr65 is bust.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top