Heating only works when hot water is enabled - WTF?

Joined
4 Dec 2020
Messages
8
Reaction score
0
Country
United Kingdom
Hi all,

Context:
- Worcester Bosch Greenstar 30CDi Classic System
- Hive Receiver and Thermostat

This started only recently:
- Switching heating on the thermostat in its own does not ignite boiler and provide heating
- When switching on Heating is followed by switching on Hot Water, then we have heating working
- Even if leaving BOTH Heating and Hot water ON together, after around 15 minutes heating stops anyway

Some observations:
- I have replaced Hive Receiver front plate, so I'm confident that signals are transmitted to boiler correctly
- Boiler shows no errors
- Heating system pressure is fine
- If heating at least sometimes works, then this is not with pumps or anything?

I can't figure out what is happening - please please can anyone help with any advice?
 
Sponsored Links
faulty central heating motorised valve its opening but not making the microswitch to bring boiler on ,
 
put a pic up of your airing cupboard where the valves are
 
Sponsored Links
faulty central heating motorised valve its opening but not making the microswitch to bring boiler on ,

Can you suggest which part exactly should be replaced:
- Diverter Valve (body, actuator, motor)
- Hydraulic Valve
 
Pictures. Sorry for the mess.
 

Attachments

  • 20201204_083212.jpg
    20201204_083212.jpg
    186.3 KB · Views: 302
  • 20201204_083232.jpg
    20201204_083232.jpg
    302 KB · Views: 284
  • 20201204_083247.jpg
    20201204_083247.jpg
    209.1 KB · Views: 279
  • 20201204_083304.jpg
    20201204_083304.jpg
    215.2 KB · Views: 308
Well, you've managed to miss it in all your photos, but you're looking for the other one of these...

sketch-1607071528077.png
 
pic 3 with pump and the valve with silver head on it , its the one to heating that is faulty you can just change the head on it no need to change entire valve
 
Yes found the other one, is this it?
 

Attachments

  • Inked20201204_090258_LI.jpg
    Inked20201204_090258_LI.jpg
    332 KB · Views: 264
I think Gas112 called it correctly though and it's actually the one I drew an arrow to, rather than the other one
 
Last edited:
Might be a good idea to get that megaflo serviced as well. Looks like its been discharging through the tundish for a while.
 
UPDATE: I have changed the powerhead the same day on Friday, and it all worked like a charm!!!

But - midday today I'm afraid this is all over again - no reaction to thermostat signals. the new powerhead is somewhat warm, even if the underlying pipes are cold.

Please guys, any further advice on this?

Maybe that's something with wiring and I should rewire the whole box below? It really has 4-5 wires coming into the same slot at times..
How would I test the powerhead is operational?

upload_2020-12-7_18-40-22.png
 
Looks like the hot water valve was closed despite the fact it was switched on. So replacing the other one as well. Will replace just a motor (£15 instead of £50 for the whole powerhead).
 