The problem I have is the boiler will lift the temperature of the radiators to between 50-60 degC, then goes to standby and the returns and hold the radiators at the this temperature for a while. After a short period of time the goes back into standby mode then lights up again for 2-3 minutes and back to standby. At this point the radiator temperature drops down to temperatures 23-35degC.
The room temperature is 19 degC measured with digital thermometer and the wall thermostat is at 25 degC.
The temperature at the pump is 43 degC. The pump is a new Grundfos 15/15 operating in position 3.
The boiler thermostat is set a number 4.
If the boiler thermostat is set to maximum the over temperature button pops out.
If I turn the hot water temperature up to 70 degC and switch on the demand for hot water the boiler lights and will lift the radiator temperature back up to 50-60 degC.
The following readings were taken with the central heating switched on and hot water off.
At the start and switching the boiler
Elected Rad = 20 DegC
Room Temp = 18 DegC
Room Thermostat = 30 DegC
Boiler Left Pipe (facing boiler) = 30 DegC
Boiler Right Pipe (facing boiler) = 43 DegC
Boiler Setting = 4
After 10 minutes
Boiler Left Pipe (facing boiler) = 49 DegC
Boiler Right Pipe (facing boiler) = 45 DegC
Elected Rad = 40 DegC
Room Temp = 18 DegC
Room Thermostat = 30 DegC
After 55 minutes
Boiler Left Pipe (facing boiler) = 56 DegC
Boiler Right Pipe (facing boiler) = 40 DegC
Elected Rad = 29 DegC
Room Temp = 18 DegC
Room Thermostat = 30 DegC
After 80 minutes
Boiler Left Pipe (facing boiler) = 57 DegC
Boiler Right Pipe (facing boiler) = 29 DegC
Elected Rad = 25 DegC
Room Temp = 18 DegC
Room Thermostat = 30 DegC
After 92 minutes
Boiler Left Pipe (facing boiler) = 54 DegC
Boiler Right Pipe (facing boiler) = 32 DegC
Elected Rad = 20 DegC
Room Temp = 18 DegC
Room Thermostat = 30 DegC
The following readings were taken with the central heating switched on and hot water on.
Boiler Left Pipe (facing boiler) = 58 DegC
Boiler Right Pipe (facing boiler) = 53 DegC
Boiler Setting = 4
Elected Rad = 40 DegC
Room Temp = 18 DegC
Room Thermostat = 30 DegC
The readings for the boiler feed and return pipes were taken directly between the rubber grommet and the wall of the pipe.
All readings were taken with a new digital probe.
Once the hot water is turned on the boiler will and deliver good central heating with consistency. If the hot water is switched off the problem returns.
Any advice would be very much appreciated.
The room temperature is 19 degC measured with digital thermometer and the wall thermostat is at 25 degC.
The temperature at the pump is 43 degC. The pump is a new Grundfos 15/15 operating in position 3.
The boiler thermostat is set a number 4.
If the boiler thermostat is set to maximum the over temperature button pops out.
If I turn the hot water temperature up to 70 degC and switch on the demand for hot water the boiler lights and will lift the radiator temperature back up to 50-60 degC.
The following readings were taken with the central heating switched on and hot water off.
At the start and switching the boiler
Elected Rad = 20 DegC
Room Temp = 18 DegC
Room Thermostat = 30 DegC
Boiler Left Pipe (facing boiler) = 30 DegC
Boiler Right Pipe (facing boiler) = 43 DegC
Boiler Setting = 4
After 10 minutes
Boiler Left Pipe (facing boiler) = 49 DegC
Boiler Right Pipe (facing boiler) = 45 DegC
Elected Rad = 40 DegC
Room Temp = 18 DegC
Room Thermostat = 30 DegC
After 55 minutes
Boiler Left Pipe (facing boiler) = 56 DegC
Boiler Right Pipe (facing boiler) = 40 DegC
Elected Rad = 29 DegC
Room Temp = 18 DegC
Room Thermostat = 30 DegC
After 80 minutes
Boiler Left Pipe (facing boiler) = 57 DegC
Boiler Right Pipe (facing boiler) = 29 DegC
Elected Rad = 25 DegC
Room Temp = 18 DegC
Room Thermostat = 30 DegC
After 92 minutes
Boiler Left Pipe (facing boiler) = 54 DegC
Boiler Right Pipe (facing boiler) = 32 DegC
Elected Rad = 20 DegC
Room Temp = 18 DegC
Room Thermostat = 30 DegC
The following readings were taken with the central heating switched on and hot water on.
Boiler Left Pipe (facing boiler) = 58 DegC
Boiler Right Pipe (facing boiler) = 53 DegC
Boiler Setting = 4
Elected Rad = 40 DegC
Room Temp = 18 DegC
Room Thermostat = 30 DegC
The readings for the boiler feed and return pipes were taken directly between the rubber grommet and the wall of the pipe.
All readings were taken with a new digital probe.
Once the hot water is turned on the boiler will and deliver good central heating with consistency. If the hot water is switched off the problem returns.
Any advice would be very much appreciated.