Sorry, here goes.
1. Do not run cable in insulation unless it is sufficiently derated.
2. not normally a good idea to terminate SWA to back of a recessed backbox, because theres no access to gland it. I bet yours isnt glanded.
3. if the living room socket is RCD protected (it should be, given the addition to the circuit), theres no purpose to the extra RCD in the shed.
4. Also what you probably have is curently very unsafe, because I bet its in 2.5mm. 2.5mm is ok for ring mains, because theres 2 of them, but for a spur to more than one socket (what you have) it is too small, because it can only carry 25 amps AT BEST. It should have a 13 amp fuse protecting it. I hope the man who connected it has good PLI for when your house burns down.
5. Spurring from a socket for an outhouse is a bodge. Its allowed, but not how you describe. garage CU's have their place, but on a ring main spur is not one of them.
In short, theres a whole lot more to electrical installation in a shed then you imply. Did you export a TNCS earth? Are there any extraeneous conductive parts in the shed? What is the distance to the shed and what is the volt drop along your supply cable? Was the installation tested? Do you have paperwork?[/quote
thankyou for you reply steve i have removed my post i should have not given advice on wiring mine was done by a electrician it took 7 hrs to do i just looked at pic of products on
screwfix that looked similar i do get your point from now on i will just stick to changing plugs from now on good to know if i need any advice will give you a buzz cheers