Is there anything I can do about a high Zs reading on a 3 bedroom house ring circuit. I've done some work in this property and I've extended the existing ring circuit. The property is approximately 20 years old and only has 1 ring circuit for the whole house which includes the kitchen. The fuse board has been upgraded to comply with the 17th edition Regs. and all the earth bonding is up to date. Most of the tests I have done are fine but the Zs for the ring circuit was 1.43ohms.
This circuit is on a 32A type B MCB and also protected by a 30MA RCD. Is there anything I can do to rectify the high Zs reading?
Please also note that the insulation resistance between N-E for this circuit was only 3.13Megohms and the Ze for the property was 0.58ohms if this helps answer my question. Many thanks.