Hive from Potterton EP2002 and heating pump now not running

SEF

Joined
5 Jan 2019
Messages
3
Reaction score
0
Country
United Kingdom
Hi all, first time poster.
I replaced my Potterton EP2002 with a hive system yesterday and seem to have a problem that the pump isn’t running, was fine a few hrs earlier before I installed the Hive.
My old system had no thermostat and just used thermostatic radiator valves and the timer on then Potterton. I’ve just recently moved in and didn’t like the set up.
The hive installation was ok if a bit fiddly with numerous cables to the Potterton as per the first poster.
It’s has all connected etc but the boiler only stays on for around 30seconds before clicking off?
It was fine prior to the hive and recently serviced.
I now have a very cold house and I’m not sure what I’ve done wrong but am very keen to get the heating running again ASAP
I followed the guides on this forum and all wired seem to be in correct places like for like where applicable.
Anyone else had a similar issue ?
I stupidly forgot to photograph my original set up so can’t easily revert it.
Thanks in advance
Steve




Read more: https://www.diynot.com/diy/threads/...ing-and-hot-water.470685/page-3#ixzz5bowq42PX
 
Last edited:
Sponsored Links
In case anyone reads the post and wonders what the issue was, a loose N was the culprit on the pump cable terminal to the hive
All working now
 