Hi All,
I'm planning on changing my existing free-standing cooker for a 7.2kW induction hob and a 3kW integrated oven (not bought yet, but I'm trying to do some forward-planning). The existing cooker has a 6mm T&E cable running to a dual outlet plate. There is then a CCU and a run of 8m (1.5m in metal conduit under plaster and 6.5m in ceiling void) of 10mm T&E to the CU, with a 32A MCB (& an RCD covering a number of circuits).
So, that gives (with 0 diversity and ignoring volt drop) a max current of 42.5A which is fine for the 10mm cable & would mean a change of the MCB to 45A.
Basically, I'm wondering about what to do "downstream" of the outlet plate, as I'm assuming the flexes on the appliances will be less than 10mm. If the oven has 2.5mm then the 45A MCB would be overrated for the max current the flex can take but of course the oven will never draw nearly that much. However, I assume that the possibility of a fault with the oven and/or cable means that I need to fit an FCU after the outlet plate.
Fine so far, but is it actually possible to fit 10mm cores into the supply side of an FCU and, if not, where am I going wrong?
Thanks for any advice/pointers,
Adam
I'm planning on changing my existing free-standing cooker for a 7.2kW induction hob and a 3kW integrated oven (not bought yet, but I'm trying to do some forward-planning). The existing cooker has a 6mm T&E cable running to a dual outlet plate. There is then a CCU and a run of 8m (1.5m in metal conduit under plaster and 6.5m in ceiling void) of 10mm T&E to the CU, with a 32A MCB (& an RCD covering a number of circuits).
So, that gives (with 0 diversity and ignoring volt drop) a max current of 42.5A which is fine for the 10mm cable & would mean a change of the MCB to 45A.
Basically, I'm wondering about what to do "downstream" of the outlet plate, as I'm assuming the flexes on the appliances will be less than 10mm. If the oven has 2.5mm then the 45A MCB would be overrated for the max current the flex can take but of course the oven will never draw nearly that much. However, I assume that the possibility of a fault with the oven and/or cable means that I need to fit an FCU after the outlet plate.
Fine so far, but is it actually possible to fit 10mm cores into the supply side of an FCU and, if not, where am I going wrong?
Thanks for any advice/pointers,
Adam