Evening all,
We're currently looking at replacing our single oven to a double. We have an electric hob which has a max rating of 6.2KW (~27A) and the new oven has a max rating of 4.1KW (~18A). Both of these are fed from a 6mm twin and earth cable and 32A breaker. The distance from the CU to the hob/oven is 6m and is within trunking buried in the solid floor.
My question is, would the 6mm twin and earth cable be sufficient for the new oven and the hob?
I found an article on something similar to this question and they showed a diversity calculation so i did the same and got the following:
6.2KW/230V = 27A (hob)
4.1KW/230V = 18A (oven)
27+18 = 45A total
Now take first 10A and add 30% of remaining load:
10+(35x30%) = 20.5A
Does this appear correct? If so then i'm hoping that our current 6mm cable and 32A breaker is still okay?
Any help would be much appreciated
Kind Regards
Sam
We're currently looking at replacing our single oven to a double. We have an electric hob which has a max rating of 6.2KW (~27A) and the new oven has a max rating of 4.1KW (~18A). Both of these are fed from a 6mm twin and earth cable and 32A breaker. The distance from the CU to the hob/oven is 6m and is within trunking buried in the solid floor.
My question is, would the 6mm twin and earth cable be sufficient for the new oven and the hob?
I found an article on something similar to this question and they showed a diversity calculation so i did the same and got the following:
6.2KW/230V = 27A (hob)
4.1KW/230V = 18A (oven)
27+18 = 45A total
Now take first 10A and add 30% of remaining load:
10+(35x30%) = 20.5A
Does this appear correct? If so then i'm hoping that our current 6mm cable and 32A breaker is still okay?
Any help would be much appreciated
Kind Regards
Sam