Hello,
I know this comes up all the time, but I've looked around and have found conflicting answers and differing scenarios, so I had to ask as I've had a little electrical experience but I'm by no means a expert.
Ok, we've decided to opt for an induction hob and separate double oven, and in our naivety bought without looking, and now it comes to installing it we've struck a snag.
The hobs is a Kenwood KHC604-Ind rated at 7,400w and the oven is a NEFF U12S53N3GB rated at 4,900w.
From what I've found out - and please correct me if I'm wrong - it goes a little something like this...
7400/230 = 32.17 amps
4900/230 = 21.3 amps
...and as we only have a single 32A cooker outlet plate connection, can't both be run from it.
This is what I'm not sure of. I've seen a number of people advise that if diversity is applied to the oven it will be (10+30% of remainder) 13amps and can therefore be connected to the normal kitchen circuit? I'm a little dubious as I would have thought that if this is the case it would have a normal plug? (The manufactures instructions say that diversity can't be applied to the hob).
Logic is telling me that we'd have to run a second circuit from the fuse box around the kitchen (approx 10m) and install a new connection point to accommodate the oven (is it just that simple?), but if there is a way that we can run both from the existing single point, we'd love to hear it.
Thanks for your time, any advice would be more than welcome.
I know this comes up all the time, but I've looked around and have found conflicting answers and differing scenarios, so I had to ask as I've had a little electrical experience but I'm by no means a expert.
Ok, we've decided to opt for an induction hob and separate double oven, and in our naivety bought without looking, and now it comes to installing it we've struck a snag.
The hobs is a Kenwood KHC604-Ind rated at 7,400w and the oven is a NEFF U12S53N3GB rated at 4,900w.
From what I've found out - and please correct me if I'm wrong - it goes a little something like this...
7400/230 = 32.17 amps
4900/230 = 21.3 amps
...and as we only have a single 32A cooker outlet plate connection, can't both be run from it.
This is what I'm not sure of. I've seen a number of people advise that if diversity is applied to the oven it will be (10+30% of remainder) 13amps and can therefore be connected to the normal kitchen circuit? I'm a little dubious as I would have thought that if this is the case it would have a normal plug? (The manufactures instructions say that diversity can't be applied to the hob).
Logic is telling me that we'd have to run a second circuit from the fuse box around the kitchen (approx 10m) and install a new connection point to accommodate the oven (is it just that simple?), but if there is a way that we can run both from the existing single point, we'd love to hear it.
Thanks for your time, any advice would be more than welcome.