Hi all,
I've read with interest some recent posts about eleccy ovens, but I just have a quickie.
My cooker was put on the 4 or 6mm² cooker radial with a 40 A MCB. As it's power rating is 2550 max.(fully absorbed, whatever that means), & so drawing only 11/12A, can I just put a 16A MCB on it instead of adding a 13A fcu?
Or if it HAS to be on a 13A fcu, can this fcu replace the old cooker switch with 1G socket?
Cheers,
Julian