I've had the CM927 for about 3 years and it has always worked well. I have a gas fired Halstead boiler (~28 Kw heat input) which is about 12 years old - not a condensing boiler.
3 years is long enough to get meaningful info. 28kW is a big boiler - unless you have a combi.
The overnight temperature on the CM927 is set at 15C.
That's shot down one theory - that 14C was above the normal night temperature, so the boiler would be on longer. However 14C is fairly high for an empty house, all you are doing is preventing it freezing. I set mine to 5C whenever I go away.
The house is well insulated and holds heat very well.
In that case you should not even need it set to 15C overnight.
My house is also well insulated and the overnight temperature is set to 5C. The overnight temperature dropped the other day from 21C to 16C, when it was about -1 outside.
I realised today that I had set the boiler stat back during the summer so I have put this back to 'normal' setting. (I'm working on the principle that higher flow temperature will result in more rapid room heating and therefore reduced boiler firing time. There's a logic there somewhere!!)
I reckon you have found the real cause of your 'problem'!
The low flow temperature will reduce radiator output, so the house will take longer to heat up and might not reach the required temperature if it is very cold outside.
As an example, a '1kw' radiator (measured at 75C/65C) will only produce 620W when running at 60C/50C.
I also noticed that there was frequent short cycling of the system with the boiler firing for a minute or so. The firing cycle was so short that there was no significant heat input to the radiators.
How do you know there was no significant heat input? These thermostats maintain the room temperature within very close limits (±0.5C). If, for example, you need 21kW to heat the house from -1C to 20C you will only need 0.5kW to raise the temperature from 19.5C to 20C.
I have now set the cycles per hour (2:Cr) to 3, and the minimum boiler on time (1:Ot) to 5 minutes.
If your boiler is a high water content/cast iron heat exchanger 3 cph may be OK.
Do you have motorized valves (obviously not if you have a combi)? These can cause problems due to the time they take to move from open to closed. I have my min on time set to 2 minutes because of this.
Is the bandwidth still set to 1.5C? As your house is well insulated you could try increasing it and see what effect it has.