Apologies for the rather long post....
My Y-plan central heating/hot-water system uses a Honeywell V4073A mid- position diverter valve. I've previously had to replace this unit once or twice in the 35+ years that I've lived here and on previous occasions I've had no problems.
I recently found that the valve had stuck in its mid position so, whenever the boiler fired up, I was getting hot water and heating.
I ordered a V4073A from Screwfix and fitted the ball plate and powerhead assembly from the new valve onto the old body. I didn't want to replace the complete valve because the pipework is a tangled mess, so undoing the unions and getting the valve body out would be a nightmare.
As it turns out it was the ball and plate assembly that had seized. but I replaced everything except the body.
On powering it all up I found that the new powerhead was 'hunting' when required to move to the mid position. This resulted in a regular 'click-click' every second or so as the mid-position sensing microswitch was activated, but the valve position then moved back slightly - enough to de-activate the microswitch whiuch then in turn caused the valve to move towards the mid position again. This cycle continued for as long as the valve was required to be in the mid position.
I'm pretty sure my other 4073A diverters have not done this. I suspect that the resultant constant jiggling of the motor cog on the rack would quickly wear out both components. When it's doing this 'hunting' thing at the mid position, the angle of movement of the valve actuator spindle is tiny, but it's enough to cause the microswitch to change state.
I found a couple of documents on the web that describe how the valve works. My understanding is that in the mid-position the valve is fed with a voltage (via a diode and a couple of resistors) that has a DC component. This stalls the motor in the mid position but provides it with enough energy to balance the effect of the springs trying to return it to the normal 'central heating port closed' position.
From what's happening on this new valve, it appears that either the spring force is too strong or the stalling current is too weak to balance the valve in the mid-position and hold it stationary. The result is that it keeps moving slightly back from the mid-position causing the microswitch to apply full power to the motor to restore it to mid-position, and so on.
I put the old powerhead back on the valve and it works fine. It moves to the mid position and there is no hunting at all. The only thing that is different to the new one is that it doesn't spring back to the 'central heating port closed' position when the power is turned off, whereas when I tried the powerhead from the new valve it always returns under the force of the springs when power is removed. I should stress that although the old valve doesn't spring back when power is removed, it does work in all modes - hot water, heating, or both.
From what I've read about how these valves work, it appears that the DC holding current is designed to be low in order to avoid permanently magnetising the components of the motor. It struck me that an old unit may inevitably become slightly magnetised - with the result that it would become harder for the springs to pull it back to the normal powered off position. Presumably the same effect might reduce the likelihood that the valve will 'hunt' in the mid position? Also, I suppose, the springs are eventually going to weaken a little on an old unit.
Do you think that's why my old valve doesn't return under spring force when the power is switched off - a combination of weakening springs and some permanent magnetisation of the motor?
Initially I thought the fault with the new valve might be because I had mis-wired it, but I've since checked the wiring over and over again. I know it is right. Besides, it matches my records of how the earlier valves were wired.
So, my question is, is it commonplace for these valves to hunt in the mid position when new, and do they eventually settle down to work normally?
Or have Screwfix sent me a faulty unit?
Thanks for any advice you can offer,
Mike
My Y-plan central heating/hot-water system uses a Honeywell V4073A mid- position diverter valve. I've previously had to replace this unit once or twice in the 35+ years that I've lived here and on previous occasions I've had no problems.
I recently found that the valve had stuck in its mid position so, whenever the boiler fired up, I was getting hot water and heating.
I ordered a V4073A from Screwfix and fitted the ball plate and powerhead assembly from the new valve onto the old body. I didn't want to replace the complete valve because the pipework is a tangled mess, so undoing the unions and getting the valve body out would be a nightmare.
As it turns out it was the ball and plate assembly that had seized. but I replaced everything except the body.
On powering it all up I found that the new powerhead was 'hunting' when required to move to the mid position. This resulted in a regular 'click-click' every second or so as the mid-position sensing microswitch was activated, but the valve position then moved back slightly - enough to de-activate the microswitch whiuch then in turn caused the valve to move towards the mid position again. This cycle continued for as long as the valve was required to be in the mid position.
I'm pretty sure my other 4073A diverters have not done this. I suspect that the resultant constant jiggling of the motor cog on the rack would quickly wear out both components. When it's doing this 'hunting' thing at the mid position, the angle of movement of the valve actuator spindle is tiny, but it's enough to cause the microswitch to change state.
I found a couple of documents on the web that describe how the valve works. My understanding is that in the mid-position the valve is fed with a voltage (via a diode and a couple of resistors) that has a DC component. This stalls the motor in the mid position but provides it with enough energy to balance the effect of the springs trying to return it to the normal 'central heating port closed' position.
From what's happening on this new valve, it appears that either the spring force is too strong or the stalling current is too weak to balance the valve in the mid-position and hold it stationary. The result is that it keeps moving slightly back from the mid-position causing the microswitch to apply full power to the motor to restore it to mid-position, and so on.
I put the old powerhead back on the valve and it works fine. It moves to the mid position and there is no hunting at all. The only thing that is different to the new one is that it doesn't spring back to the 'central heating port closed' position when the power is turned off, whereas when I tried the powerhead from the new valve it always returns under the force of the springs when power is removed. I should stress that although the old valve doesn't spring back when power is removed, it does work in all modes - hot water, heating, or both.
From what I've read about how these valves work, it appears that the DC holding current is designed to be low in order to avoid permanently magnetising the components of the motor. It struck me that an old unit may inevitably become slightly magnetised - with the result that it would become harder for the springs to pull it back to the normal powered off position. Presumably the same effect might reduce the likelihood that the valve will 'hunt' in the mid position? Also, I suppose, the springs are eventually going to weaken a little on an old unit.
Do you think that's why my old valve doesn't return under spring force when the power is switched off - a combination of weakening springs and some permanent magnetisation of the motor?
Initially I thought the fault with the new valve might be because I had mis-wired it, but I've since checked the wiring over and over again. I know it is right. Besides, it matches my records of how the earlier valves were wired.
So, my question is, is it commonplace for these valves to hunt in the mid position when new, and do they eventually settle down to work normally?
Or have Screwfix sent me a faulty unit?
Thanks for any advice you can offer,
Mike