honeywell y plan

Joined
10 Apr 2006
Messages
3
Reaction score
0
Location
Dumfriesshire
Country
United Kingdom
Hi, I am intending upgrading the controls on my heating system, currently there is a Sangamo M8 which gives no control of the DHW. I intend to use a honeywell 3 port mid position valve. honeywell L641A cylinder stat, a honeywell CM 927 wireless programmable room stat and a WickesRWB9 (already have this from a former installation) to control the timing for the DHW. I would appreciate your advise as to how to wire the wickes controller for my situation. I have got lots of good info from the Honeywell website regarding the wiring of their components.
thanking you in anticipation..
 
Sponsored Links
CH ON at RWB9 to room thermostat switch, then from room thermostat switch to white wire on valve.

HW ON at RWB9 to cylinder stat common.

HW OFF at RWB9 to grey wire on valve.

Call, on cylinder stat to orange wire on valve.

Satisfied, on cylinder stat to grey wire on valve.

Switched live to boiler connected to orange on valve.
 