Hello All,
Just like a sanity check on a CH thermostat replacement exercise. I'm replacing a Horstmann Centaurplus C17 thermostat with a Hive V2 single channel receiver. Simple controls - there is no room thermostat currently, just thermostatic rad valves on all bar one radiator, no hot water circuit. Current backplate can be re-used, after some wiring connections have been changed.
Existing wiring similar to first diagram (except 4 just goes to boiler/pump Live).
Hive connection info:
Now, as there is no current connection for Heating Off I reckon I can do the following:
Earth, N, L - No change
Common - move from 2 to 1
Heat On - move from 4 to 3
Is this right? All (helpful) comments welcome. Thanks.
(edited to correct typo)
Just like a sanity check on a CH thermostat replacement exercise. I'm replacing a Horstmann Centaurplus C17 thermostat with a Hive V2 single channel receiver. Simple controls - there is no room thermostat currently, just thermostatic rad valves on all bar one radiator, no hot water circuit. Current backplate can be re-used, after some wiring connections have been changed.