Have a fully pumped system with a three port valve. Rads getting hot when hot water only is selected. Have already changed three port valve. Please help - getting desperate !
Complete valve was changed this week. Fault occured overnight approximately one month ago - working fine until that point. System approximately 15-20 years old in microbore. Boiler is fan assisted. Anything else you need to know ?
DO check the pump is pumping towards the middle connection. They work to varying extents backwards, but always end up "letting by". Could have always been wrong.