Ok here goes, ready, steady...................... GOoooooo.
Ok advise time.
Been out of the electrical game now for over 20 years no interested in returning as I'll basically have to start from fresh anyway question.
Installing a hot tub in my summer house with its own feed and I cant remember what's what so hence why I'm here.
The tub is rated at either 16amp or 32amp dependent if you want to run the heater with the blower so my plan is to run it as 32amp as follows...
Old type rewritable DB protected by RCD with a spare carrier, this spare I'm going to use a 32amp MCB and run 10mm 6242Y T&E up from the DB into the attic, through the attic and terminated feeding armoured SWA.
Now specs says that if the "Above a plasterboard ceiling covered by thermal insulation, insulation thickness greater than 100 mm" then the 10mm is sufficient the run length in 6242Y is 20mtrs and armoured outside clipped is 15mtrs terminated into a Locking Off Safe Shut Down - IP41 IP65 isolator.
The calcs says:
70°C Thermoplastic Insulated and Sheathed Flat Cable with Protective Conductor
Tables Apply to: 6241Y, H6242Y, H6243Y
Voltage: 230V
Load: 7.36kW / 32A
Length: 20m
Method of Installation: H6242Y ONLY above a plasterboard ceiling covered by thermal insulation exceeding 100mm in thickness
Cable Size: 10mm²
And....
Multicore 90°C Armoured Thermosetting Insulated Cables
Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,
Voltage: 230V
Load: 7.36kW / 32A
Length: 15m
Method of Installation: Clipped direct
Cable Size: 2.5mm²
So would I be ok to carry out the above?
Or can anyone that's up to date enlighten me?
Regards
Ok advise time.
Been out of the electrical game now for over 20 years no interested in returning as I'll basically have to start from fresh anyway question.
Installing a hot tub in my summer house with its own feed and I cant remember what's what so hence why I'm here.
The tub is rated at either 16amp or 32amp dependent if you want to run the heater with the blower so my plan is to run it as 32amp as follows...
Old type rewritable DB protected by RCD with a spare carrier, this spare I'm going to use a 32amp MCB and run 10mm 6242Y T&E up from the DB into the attic, through the attic and terminated feeding armoured SWA.
Now specs says that if the "Above a plasterboard ceiling covered by thermal insulation, insulation thickness greater than 100 mm" then the 10mm is sufficient the run length in 6242Y is 20mtrs and armoured outside clipped is 15mtrs terminated into a Locking Off Safe Shut Down - IP41 IP65 isolator.
The calcs says:
70°C Thermoplastic Insulated and Sheathed Flat Cable with Protective Conductor
Tables Apply to: 6241Y, H6242Y, H6243Y
Voltage: 230V
Load: 7.36kW / 32A
Length: 20m
Method of Installation: H6242Y ONLY above a plasterboard ceiling covered by thermal insulation exceeding 100mm in thickness
Cable Size: 10mm²
And....
Multicore 90°C Armoured Thermosetting Insulated Cables
Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,
Voltage: 230V
Load: 7.36kW / 32A
Length: 15m
Method of Installation: Clipped direct
Cable Size: 2.5mm²
So would I be ok to carry out the above?
Or can anyone that's up to date enlighten me?