House not warm enough Vaillant thermocompact 142Eh

Joined
12 Feb 2017
Messages
5
Reaction score
0
Country
United Kingdom
Vaillant thermocompact 142Eh (I know it is old) during this cold weather cannot heat my house enough. Any ideas as to why.

The boiler was checked a while ago... cleaned/gas pressure tested/flame checked for low startup then full flame etc.

Temp gauge says 70 c during this cold weather but it goes higher in the mild sessions we have had.

The actual plumbing of the radiators is the old single pipe with two risers that connect the radiators to the single pipe that runs round the house and back to the boiler.

The system has not changed since we have had much colder winters apart from a towel rail; the towel rail has been connected in the same fashion e.g. using single pipe system with two risers. I cannot see the addition of the towel rail putting much extra load on the CH system as it is throttled to just allow enough water to keep the towel rail warm.
 
Last edited:
Sponsored Links
What is the flow and return temperature at the boiler?

That model should be well capable of giving a flow of 80 C.

What position is the rad temperature knob on the boiler?

Tony
 
Hi Tony,
The rad temperature knob on the boiler is max (9)

What is the flow and return temperature at the boiler?

Using an old office wall type thermometer with the bulb touching near the Service cocks, I get 102 f/38 c on the Flow and 74 f/23 c Return.
Can I assume from the above that the Vaillant temperature gauge reads the Return from the radiators? So this explains why the Vaillant temperature gauge will go higher in warmer weather.

What type temperature gauge do you people use?
 
Sponsored Links
Normally no; I left the heating on all night then they were too hot to touch this morning and the gauge on the boiler now reads 90c
 
Last edited:
It does sound like the boiler is taking an age to heat the water to 90C. Once there, I Imagine the radiators do their job and warm the house OK?

Measuring flow and return temperatures off the pipe is done with and IR gun or a probe that can be attached to the copper. A traditional thermometer won't get an accurate reading. It could be helpful to have the return temperature, but perhaps not all that helpful.
 
It does sound like the boiler is taking an age to heat the water to 90C. Once there, I Imagine the radiators do their job and warm the house OK?
Not really, that's why I'm trying to track down the fault ;)

I've ordered an IR gun so that I can check this sort of stuff and anything else around the house.
 
I've ordered an IR gun so that I can check this sort of stuff and anything else around the house.
IR guns will give false (low) readings if pointed at bare copper pipes; painted is OK.

The easiest way of getting consistent readings is to wrap some insulating tape round the pipe and hold the gun against the tape.
 
IR meters are pretty useless except on matt black finish.

Needs a K-Type thermocouple contact meter!

Seems the boiler power output is seriously low.

When was it last properly serviced?

Tony
 
IR meters are pretty useless except on matt black finish.
The colour is not important. Matt white paint has virtually the same emissivity as matt black. The same is true of insulating tape. It's not the colour which is important but how reflective it is. That's why shiny new copper pipe has a very low emissivity (0.03) but oxidised copper has an emissivity of 0.78. A mirror has an emissivity of 0.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top