How deep does cable need to be buried?

Joined
22 Sep 2005
Messages
6,591
Reaction score
76
Location
Preston, Lancashire
Country
United Kingdom
Running an armoured cable from consumer unit in the house to a shed to provide power. Two questions.
1. How deep does the cable need to be buried?
2. What's the best way of making a deep channel whilst minimising the damage to a lawn?
 
Sponsored Links
2, mini jcb, no i am not joking (other brands of back hoe diggers are avaiable)
 
450mm.

No doubt someone can post a diagram of how you back fill the hole, but you need warning tape etc...
 
As securespark has said 450mm as a minimum (told by an old seb boy it's wellyboot depth), bottom of trench put a bed of sand (fills any dips in trench base) then snake the swa along the trench (puts slack into swa & saves it getting pulled taught ) Then backfill to 100mm below surface, lay warning tape now finish backfilling.
 
Sponsored Links
minimising damage to the lawn:

carefully cut up THICK turfs and move them to one side. Then do the deep digging and use a sheet or something to put the soil on.

and rememeber to heavilly compress the soil when backfilling or the strip of lawn you opened up will sink.
 