Gloworm Spacesaver boiler red light indicating low water pressure. The setting when i first checked was way below 1bar and after filling up to just over 1bar the light is still on so im guessing switch needs replacing. Thanx to any advice.
Yeah i turned it off on the system and the mains and left it for a while then went through all the necessary checks. All radiators are calling for heat , thermostat, etc and the red under pressure light's still on.
I guess you have the glowworm spacesaver complheat.
The low pressure switch is on the left hand side next to the return pipe. Release the system pressure through a drain point, note which wire is on which terminal and unsrew, replace or clean out old with a pin, put a few wraps of PTFE round thread and screw back in