John, I think you need to re-think the difference between the L-N impedance & Zs. If the (acceptable) L-N impedance really was as high as 1R then the PSSC would be in the order of 230A for a L-N bolted short circuit. This magnitude of fault current is only just acceptable for a B32A MCB and would not be acceptable for a C32A or anything bigger to obtain a 5s disconnection time.
I don't need to re-think anything - as I explain at the end of this post, I think you are talking at 'cross purposes' with what I've been saying. What you describe is
exactly what I was talking about - a final circuit that only just had a low enough Zs to satisfy the requirements of a B32 (which is very probably what the OP's ring final is protected by).
The value of the L-N impedance needs be significantly less than Zs for a workable supply, otherwise, as you have calculated, volt drops will be intolerable. 13V drop for a 3kW load is unacceptable. ...
You may call it 'unacceptable' but L-N and L-E ('Zs') loop impedances will only differ by virtue of the difference between the impedances of the N and E paths back to the transformer. In a TN-C-S installation they will, by definition, be identical at the origin of the installation, and very similar when view from loads on final circuits which are close to the origin/CU.
As for 'not acceptable', a 13V VD (resulting from my arbitrarily chosen example figures) is only slightly more than the 'guidance' figure of 5% maximum suggested in the regs, and the VD within the installation would then be appreciably under 5%.
Consider the volt drop that would be experienced by a 10kW electric shower and what its true output would become if the supply impedance really was about 1R.
Both Zs and L-N impedance (at the shower) would obviously be much lower for a shower circuit than the ring final we were discussing. Again, the circuit would be designed so that the VD under load was acceptable (in terms of the 'guidance' 5% in the regs, or whatever)
As food for thought.... consider the max Zs for a PME supply..... Zs, for a PME service, is, in effect, the L-N impedance. The max acceptable value for Zs on PME is 0.35R.
Ah, I think I see your problem - you are seemingly thinking about the situation (loop impedances and voltage) at the
origin of an installation, not at the end of a final circuit.
Yes, at the origin of a TN-C-S installation, the EFLI ('Zs' if you want) would be a maximum of 0.35Ω. However, there could well be, say, 1Ω in the final circuit wiring of a 32A circuit, so that the Zs of the circuit at the load could be 1.35Ω (still within requirements of a B32). Assuming 2.5mm² T+E cable, if the R1+R2 of the final circuit (
at the load) were, per my example, 1Ω, then the L+N impedance ('R1+Rn') of the final circuit would be about 0.77Ω. The total L+N loop impedance
at the load would therefore be about 1.12Ω (0.35Ω+0.77Ω), hence a voltage drop (
at the load) of about 14.56V with a 13A load - even if you regarded that as 'unacceptable'.
Kind Regards, John