Todays little just job; customer has complained of frequent fuse blowing since changing to LED tubes in recent fittings from Flou.
The situation is far from domestic or DIY and in a bid to stop it happening customer recently instructed an electrician to change the submain fuse box to all AFDD Schneider, 6x 6A AFDD for lights with each running between 3.5 to 5A (total ~25A), plus 1x 16A AFDD feeding several DSSO, basically not used. It is fed with app 30m of 4mm² 3C SWA and 32A BS88.
The problem is the building is powered down daily and they expect to light it by pressing the green button (DOL starter). They don't understand: Why this wasn't a problem with their fluo light but is with LED, why the circuit fuses never blew or the new AFDDs have never tripped but the supply fuse blows sometimes and certainly don't understand inrush.
I've suggested delay step starting which they don't like the idea of as they have previously had problems with a similar system, getting the staff to switch the lights off before they close up which they describe as impossible.
I suggested upgrading the fuse and cable, However that made 2 people shudder at the thought as the building is in a row of industrial units and the submain passes through a unit to which they have very restricted access as it's supposedly sensitive/secure.
As a last resort I've suggested DOL starters on some of the circuits but their risk assessment says no (I assume due to a problem in the past).
The situation is far from domestic or DIY and in a bid to stop it happening customer recently instructed an electrician to change the submain fuse box to all AFDD Schneider, 6x 6A AFDD for lights with each running between 3.5 to 5A (total ~25A), plus 1x 16A AFDD feeding several DSSO, basically not used. It is fed with app 30m of 4mm² 3C SWA and 32A BS88.
The problem is the building is powered down daily and they expect to light it by pressing the green button (DOL starter). They don't understand: Why this wasn't a problem with their fluo light but is with LED, why the circuit fuses never blew or the new AFDDs have never tripped but the supply fuse blows sometimes and certainly don't understand inrush.
I've suggested delay step starting which they don't like the idea of as they have previously had problems with a similar system, getting the staff to switch the lights off before they close up which they describe as impossible.
I suggested upgrading the fuse and cable, However that made 2 people shudder at the thought as the building is in a row of industrial units and the submain passes through a unit to which they have very restricted access as it's supposedly sensitive/secure.
As a last resort I've suggested DOL starters on some of the circuits but their risk assessment says no (I assume due to a problem in the past).