Some advice please.
I have some high intensity lighting above an aquarium, that was wired by an electrician, but I need to check that all is well as it is a very complex job as you will see...
They consist of 3 pendants. Each pendant has 3x400W HQI bulbs and 4x 80w Fluorescent tubes.
Total of 9x400W HQI and 12x80W T5 tubes.
They were wired from a 32A RCBO in a consumer unit with 2 x2.5mm T+E out. This goes to a junction box and a 6mm T+E comes out and goes into a 100AMP switch (used just for on and off). The Live out from the switch is fed into single pole 100amp connection/ distribution block and all the individual lives are taken from this block.
There are six commercial timers that take power with 2.5mm cable from this block. The outputs of the timers (ie on /off ) are fed into 3x25 amp and 2x16 amp contactors. Each contactor has a 2.5mm cable feeding them also from the live block and these then go on to connect to waterproof sockets. Each socket is wired with 2.5mm cable and the maximum each can supply is 2x400W. The control gear plugs into the sockets and onto the pendeants as usual.
The lighting is switched on in sequence with 6 t5 tubes at 11am (from one timer channel), then the second lot of 6 t5 tubes an hour later. These are wired through the 16A contactors).
The Halides then come on in lots of three at 1pm then 1.05pm, then 1.10pm. ( so all 9 on by 1.10pm. They then switch off in a similar pattern with the t5 tubes going out last later at night.
My Q's please.
Is the 32amp Btype RCBO sufficient at the consumer unit?
Is 2x2.5mm cable ok for about a 4m distance in the roof (single storey building runs above the wall and the roof in a channel, with insulation separate from it.)
Is the junction box connecting to 6mm cable ok?.
Is it ok to have the live distribution block giving out all the individual feeds?.... is 2.5mm cable ok to feed the 25amp contactor ( powers up 3x400w each).
Is there a need to wire in another consumer unit with mcb's to supply say the clocks with a 6amp breaker, each contactor with a breaker and so on. If so, what sized breaker and type would you recommend for the 25amp contactor given the load on it ie 3x400W HQI bulbs). I am assuming the startup surge is around 1.6x rated value?....
Would appreciate your advice as initially the live block and the 100 amp switch had 2x2.5 mm cable between them and there was a loose connection that caused a little overheating. This was replaced with 6mm cable and all seems fine, but I want to check that this is the best way to have it all wired up and whether the lighting rig / all it's components should be individually fused/ RCD-MCB'd/ RCBO'd.
I appreciate this is a complex scenario, but would appreciate advice.
I am getting another electrician in to scope it all, but want a number of opinions to make sure it's top notch work and not just overkill for the sake of it.
Are all of the wires of sufficient size for the load?.
Thanks
Moserelli.
I have some high intensity lighting above an aquarium, that was wired by an electrician, but I need to check that all is well as it is a very complex job as you will see...
They consist of 3 pendants. Each pendant has 3x400W HQI bulbs and 4x 80w Fluorescent tubes.
Total of 9x400W HQI and 12x80W T5 tubes.
They were wired from a 32A RCBO in a consumer unit with 2 x2.5mm T+E out. This goes to a junction box and a 6mm T+E comes out and goes into a 100AMP switch (used just for on and off). The Live out from the switch is fed into single pole 100amp connection/ distribution block and all the individual lives are taken from this block.
There are six commercial timers that take power with 2.5mm cable from this block. The outputs of the timers (ie on /off ) are fed into 3x25 amp and 2x16 amp contactors. Each contactor has a 2.5mm cable feeding them also from the live block and these then go on to connect to waterproof sockets. Each socket is wired with 2.5mm cable and the maximum each can supply is 2x400W. The control gear plugs into the sockets and onto the pendeants as usual.
The lighting is switched on in sequence with 6 t5 tubes at 11am (from one timer channel), then the second lot of 6 t5 tubes an hour later. These are wired through the 16A contactors).
The Halides then come on in lots of three at 1pm then 1.05pm, then 1.10pm. ( so all 9 on by 1.10pm. They then switch off in a similar pattern with the t5 tubes going out last later at night.
My Q's please.
Is the 32amp Btype RCBO sufficient at the consumer unit?
Is 2x2.5mm cable ok for about a 4m distance in the roof (single storey building runs above the wall and the roof in a channel, with insulation separate from it.)
Is the junction box connecting to 6mm cable ok?.
Is it ok to have the live distribution block giving out all the individual feeds?.... is 2.5mm cable ok to feed the 25amp contactor ( powers up 3x400w each).
Is there a need to wire in another consumer unit with mcb's to supply say the clocks with a 6amp breaker, each contactor with a breaker and so on. If so, what sized breaker and type would you recommend for the 25amp contactor given the load on it ie 3x400W HQI bulbs). I am assuming the startup surge is around 1.6x rated value?....
Would appreciate your advice as initially the live block and the 100 amp switch had 2x2.5 mm cable between them and there was a loose connection that caused a little overheating. This was replaced with 6mm cable and all seems fine, but I want to check that this is the best way to have it all wired up and whether the lighting rig / all it's components should be individually fused/ RCD-MCB'd/ RCBO'd.
I appreciate this is a complex scenario, but would appreciate advice.
I am getting another electrician in to scope it all, but want a number of opinions to make sure it's top notch work and not just overkill for the sake of it.
Are all of the wires of sufficient size for the load?.
Thanks
Moserelli.